Yl-620 vfd + uc300eth 5lpt analog problem.

If you have a question about the software please ask it here.

Yl-620 vfd + uc300eth 5lpt analog problem.

Postby martomasz » Fri Jun 02, 2023 6:20 am

Hi there,

I've managed to connect and set up my 2.2kw spindle through the analogue output on the uc300eth, with analogue bob (bought from cncdrive), although I'm not getting 10v output. Only around 9.3v, that's why the vfd, which is correctly set for 400hz, only gives me +-375hz.
Is there a way to set the 0-10v output on the eth300? I was going to go with rs485 but took advice from cncdrive on this forum and went with the analogue signal generated by eth300. Thanks.
Bob to vfd has been wired 0.5mm wire, around 30 cm long.
martomasz
 
Posts: 2
Joined: Sat Apr 15, 2023 10:06 am

Re: Yl-620 vfd + uc300eth 5lpt analog problem.

Postby CT63 » Fri Jun 02, 2023 8:05 pm

You can adjust the max rpm in the VFD to compensate. I assume its 0-24,000 rpm? Actually, the additional 25hz isn't going to make a noticeable difference and probably not worth the effort.
CT63
 
Posts: 124
Joined: Sat Sep 03, 2016 11:19 pm
Location: Connecticut, USA

Re: Yl-620 vfd + uc300eth 5lpt analog problem.

Postby cncdrive » Fri Jun 02, 2023 9:44 pm

Yes, you can adjust the Volts/Hz parameter in the VFD to make it to produce 400Hz at 9.3Volts.
Also check if the PWM max. is set to 100% in the software and that the S spindle speed is programmed to the maximum possible.
cncdrive
Site Admin
 
Posts: 4887
Joined: Tue Aug 12, 2014 11:17 pm


Return to Ask a question from support here

Who is online

Users browsing this forum: No registered users and 4 guests