mrmacca wrote:Also ordered a relay.
Dazp1976 wrote:mrmacca wrote:Also ordered a relay.
This VFD yes?.
https://www.aliexpress.com/item/32924146109.html.
I'll have a look at it. May be fine without a relay but I personally would always use one (or an optocoupler module) for vfd or servo drive.
Dazp1976 wrote:cncdrive wrote:You have to connect the power ground (24V0) to the digital ground of the VFD if you driving the FWD signal of the VFD from the isolated output of the AXBB-E.
This VFD seems that it does not have a separeate analog and digital GND which is not really good, because then you have to connect the 5V0 and 24V0 together to make it work.
That is a good oversight!.
Could he try this workaround below?.
Use the non isolated outputs for switching instead.
Port1-output# to FWD and the 5VO from port1 going to GND.
Then you have 2* 5VO on shared vfd GND rather than having a 5v and a 24v?.
This is why I always suggest using a relay for switching fwd!!!!!.
Relay:
24v+ to RL+, output# to RL-.
VFD fwd to RL/NC, VFD gnd to RL/com.
(ssr are usually marked something like pin 1+&2- instead of nc/com)
Fwd+,1/gnd-,2
That solves the whole problem.
You can get a simple DC ssr relay from amazon for cheap.
Or get a cheap 2 pin switch between fwd/gnd and switch it manual.
Relay looks like this:
https://img.joomcdn.net/1ae4b792bbb5293 ... ginal.jpeg
mrmacca wrote:Can you draw me a diagram what wires go were, Im thick when it comes this this
Dazp1976 wrote:mrmacca wrote:Can you draw me a diagram what wires go were, Im thick when it comes this this
You will have to change a few parameters on the vfd first don't forget.
Max freq, to not overrun the rpm.
Min freq, to prevent creeping at 0v analog.
Control style being ued.
Etc.
5-200v Relay will be fine. As long as the voltage range being used is covered by its spec. In your case 12v/24v is covered both sides.
mrmacca wrote:Parameter setting