As Gerry already posted, changing a textfield label# is only needed for the 2017 screenset. I suggest when first setting up plugin to use the UCCNC default screen to help eliminate any other possible issues when trouble shooting.
There are many different HY plugins version out there and I suggest the latest HY14 that can be found in this thread and is the latest uploaded version. Remove any other versions and check "Enable" and
"Call Startup" for HY14. The settings below for VFD are for what's needed to use RS485, there are other settings based on spindle type that I won't go into. There's mega info on the zone for these settings.
In UCCNC spindle setup make sure PWM spindle is checked and have the correct min/max RPM.
PD001>>>>>> 02 Enable commands on port rs485
PD002>>>>>> 02 Enable speed control on port rs485
PD023>>>>>> 01 Enable reverse rotation (only if you want to run CCW)
PD163>>>>>> 1 Vfd address needs 1
PD164 >>>>>> 1 Line Speed(1 for 9600 bauds)
PD165 >>>>>> 3 8N1 RTU
After plugin is enabled with call at start up on first run a window will appear, in serial port settings of plugin there are 2 combobox's 1 for your available com's and 1 for baudrate, make sure baudrate matches
VFD settings. Press "Connect" and you will see if serial port is connected and if any communication between VFD and plugin.