sorry for fragmented information...
with mach 3 go well..
f
merlinogio wrote:Hi Dan, Ger
HY12 work when it have a good day..
screenset 2017
Hy12 configured as in instruction
Spindle talker go well (open port and go with the slider don't go with the Fixed RPM button 6000, 8000, etc)
when i open UCNC he talk with VFD that aswer (see below)
BUT
when i click M3 Nothing
sometimes it go but with fix RPM (don't change with s command)
any suggestion?
thanks in advance
flavio
Porta aperta dal processo "UCCNC.exe" (PID: 4056)
Richiesta:21/09/2018 18:41:24.38664
01 01 03 8E 00 00 5C 65 ...?..\e
Risposta:21/09/2018 18:41:24.40764 (+0.0210 seconds)
01 01 03 8E 00 64 5D 8E ...?.d]?
Richiesta:21/09/2018 18:41:25.17764 (+0.7620 seconds)
01 01 03 8E 00 00 5C 65 ...?..\e
Risposta:21/09/2018 18:41:25.19664 (+0.0190 seconds)
01 01 03 8E 00 64 5D 8E ...?.d]?
Richiesta:21/09/2018 18:41:26.96764 (+0.7630 seconds)
01 01 03 8E 00 00 5C 65 ...?..\e
Risposta:21/09/2018 18:41:26.98664 (+0.0190 seconds)
01 01 03 8E 00 64 5D 8E
Dan911 wrote:Hi flavio,
I'm in the process of rewriting this plugin so some features like amps isn't implemented yet but see if this helps.
merlinogio wrote:Hi Dan, Ger
first of all thanks for your help
the problem now it's solved changing the dongle.
if could be useful I try this:
- new dongle with driver ch341ser of 2007 year -> Hy12 NOT go, hy14 NOT go, Mach3 GO
- new dongle with driver ch341ser of 2014 year (Get link) -> Hy12 GO, Hy14 NOT go, Mach 3 GO
in the attachment the serial monitor trace in the case: mach3, UCCNC Hy14 UCCNC Hy12
I don't know the communication protocol of vfd but seems that the polling sequence are different in the three case
thanks for help I hope that the test could help..
if useful I can try to do other tests
flavio
Return to General discussion about the UCCNC software
Users browsing this forum: No registered users and 10 guests