Page 1 of 2
Soft Limit errors appear all the time
Posted:
Tue Mar 28, 2017 9:40 pm
by Guenter_Schmied
Dear CNCdrive,
I am using a UC100 + CNC4pc C11gs on a 4 axis machine.
I am getting the Softlimit error message (see picture) all the time during machining in random situations,
allthough my SoftLimits are disabled on the general settings tab. as explained on the manuals.
On all the Softlimits X-Axis , Y,Z,A configuration screens I have (softlimit -(units) : 0 +(units): 0
What can we do to resolve this issue ?
Re: Soft Limit errors appear all the time
Posted:
Wed Mar 29, 2017 5:25 am
by cncdrive
The UCCNC only checks the Softlimits if the softlimits are enabled in the General Settings.
If the softlimits coordinates positive and negative are both set to 0 and the softlimits are enabled then the softlimits condition will always met,
because the range size of the softlimits is then 0, because there is no value between coordinate 0 and 0, so basicly there will be always a softlimit trigger condition then.
So, you may set the softlimits negative to a large negative number and the positive to a large positive number, for example -100000 and +100000, if the range covers your axis range then the softlimits will never trigger.
Also have to note that the softlimits are in machine coordinates which means they are referenced to your home coordinate, so offsets does not apply for them, so make sure you homed your machine.
Or you can just disable the softlimits on the General settings page and then the softlimit function will be disabled and then it does not matter what softlimits coordinates you set.
A sidenote about this is that it is not enough that you untick the Enable softlimits checkbox, but you have the press the Apply settings button to Apply the change and you can use the Save button to save the settings and to let the UCCNC remember it the next time your will run the software.
Also you can verify in the Profile setting file if the setting is really disabled with opening the .pro file from the UCCNC/Profiles and Yourprofilename.pro, open it with a text editor and find the key I'm showing on the attached picture.
Re: Soft Limit errors appear all the time
Posted:
Fri May 19, 2017 4:44 pm
by Guenter_Schmied
Hi I posted yesterday a question regards this and the forum does not show it !
I Keep getting the same results, Softlimits engage all the time, in Default.pro it is correct
it is set to false (disabled).
I also posted 2 pictures of this, of my screen, with the softlimits error. I also did +99 million and -99million
in the softlimit boxes, as a 2ble check that they would never been fired. Nothing changed ! Keep having the
same problem again again and again !
I had this issue with v 1.2028 then I upgraded recently to 1.2037 to be shure there was not the cause of
and old version, and no solution ! All my screens with pictures are from v. 1.2038.
Ca you help me ?
Re: Soft Limit errors appear all the time
Posted:
Fri May 19, 2017 4:47 pm
by Guenter_Schmied
I will attch again pictures, hope this message get trhu
Re: Soft Limit errors appear all the time
Posted:
Fri May 19, 2017 4:52 pm
by Guenter_Schmied
I am having trouble sending pictures, this one did not submit.
Re: Soft Limit errors appear all the time
Posted:
Fri May 19, 2017 4:56 pm
by Guenter_Schmied
This is the softlimit error message it happends
aleatory with any Gcode, there is no particular one
that I can tell.
Re: Soft Limit errors appear all the time
Posted:
Fri May 19, 2017 5:03 pm
by Guenter_Schmied
Here you can see my configuration
Softlimits are disabled in my screen
as also in the Default.Pro, as you suggested
Re: Soft Limit errors appear all the time
Posted:
Fri May 19, 2017 5:44 pm
by dezsoe
Guenter_Schmied wrote:Here you can see my configuration
Softlimits are disabled in my screen
as also in the Default.Pro, as you suggested
Could you post your profile file?
Re: Soft Limit errors appear all the time
Posted:
Tue May 23, 2017 2:43 pm
by Guenter_Schmied
[Screensetsettings]
mainscreenfilename=Defaultscreenset
splashscreen=0
[axessettingscontrolX]
Axisenabled=True
Stepportnumber=1
Steppinnumber=2
Steppinnegate=False
Dirpinnumber=3
Dirportnumber=1
Dirpinnegate=False
Enapinnumber=0
Enaportnumber=0
Enapinnegate=False
Limitminuspinnumber=11
Limitminuspinnegate=True
Limitpluspinnumber=11
Limitpluspinnegate=True
Homepinnumber=11
Homepinnegate=True
Homedirectionpositive=False
Homeautozero=True
Homingvalue=0
Homingspeedup=800
Homingspeeddown=250
Stepsperunit=318.18181818
Velocity=2000
Acceleration=200
Softlimitpositive=0
Softlimitnegative=0
Backlashenable=False
Backlashdistance=0
Slaveaxis=None
Homeportnumber=1
Limitminusportnumber=1
Limitplusportnumber=1
Compaccel=240
[axessettingscontrolY]
Axisenabled=True
Stepportnumber=1
Steppinnumber=4
Steppinnegate=False
Dirpinnumber=5
Dirportnumber=1
Dirpinnegate=True
Enapinnumber=0
Enaportnumber=0
Enapinnegate=False
Limitminuspinnumber=13
Limitminuspinnegate=True
Limitpluspinnumber=13
Limitpluspinnegate=True
Homepinnumber=13
Homepinnegate=True
Homedirectionpositive=False
Homeautozero=True
Homingvalue=0
Homingspeedup=500
Homingspeeddown=250
Stepsperunit=318.181818181818
Velocity=2000
Acceleration=200
Softlimitpositive=0
Softlimitnegative=0
Backlashenable=False
Backlashdistance=0
Slaveaxis=None
Homeportnumber=1
Limitminusportnumber=1
Limitplusportnumber=1
Compaccel=240
[axessettingscontrolZ]
Axisenabled=True
Stepportnumber=1
Steppinnumber=6
Steppinnegate=False
Dirpinnumber=7
Dirportnumber=1
Dirpinnegate=False
Enapinnumber=0
Enaportnumber=0
Enapinnegate=False
Limitminuspinnumber=15
Limitminuspinnegate=True
Limitpluspinnumber=15
Limitpluspinnegate=True
Homepinnumber=15
Homepinnegate=True
Homedirectionpositive=True
Homeautozero=True
Homingvalue=50
Homingspeedup=500
Homingspeeddown=250
Stepsperunit=318.18181818
Velocity=2000
Acceleration=200
Softlimitpositive=0
Softlimitnegative=0
Backlashenable=False
Backlashdistance=0
Slaveaxis=None
Homeportnumber=1
Limitminusportnumber=1
Limitplusportnumber=1
Compaccel=240
[axessettingscontrolA]
Axisenabled=True
Stepportnumber=1
Steppinnumber=8
Steppinnegate=False
Dirpinnumber=9
Dirportnumber=1
Dirpinnegate=False
Enapinnumber=0
Enaportnumber=0
Enapinnegate=False
Limitminuspinnumber=0
Limitminuspinnegate=False
Limitpluspinnumber=0
Limitpluspinnegate=False
Homepinnumber=0
Homepinnegate=False
Homedirectionpositive=False
Homeautozero=True
Homingvalue=0
Homingspeedup=500
Homingspeeddown=250
Stepsperunit=800.020719329467
Velocity=2000
Acceleration=200
Softlimitpositive=0
Softlimitnegative=0
Backlashenable=False
Backlashdistance=0
Homeportnumber=0
Limitminusportnumber=0
Limitplusportnumber=0
Compaccel=240
[axessettingscontrolB]
Axisenabled=False
Stepportnumber=0
Steppinnumber=0
Steppinnegate=False
Dirpinnumber=0
Dirportnumber=0
Dirpinnegate=False
Enapinnumber=0
Enaportnumber=0
Enapinnegate=False
Limitminuspinnumber=0
Limitminuspinnegate=False
Limitpluspinnumber=0
Limitpluspinnegate=False
Homepinnumber=0
Homepinnegate=False
Homedirectionpositive=False
Homeautozero=True
Homingvalue=0
Homingspeedup=500
Homingspeeddown=250
Stepsperunit=200
Velocity=2000
Acceleration=200
Softlimitpositive=0
Softlimitnegative=0
Backlashenable=False
Backlashdistance=0
Homeportnumber=0
Limitminusportnumber=0
Limitplusportnumber=0
Compaccel=240
[axessettingscontrolC]
Axisenabled=False
Steppinnumber=0
Stepportnumber=0
Steppinnegate=False
Dirpinnumber=0
Dirportnumber=0
Dirpinnegate=False
Enapinnumber=0
Enaportnumber=0
Enapinnegate=False
Limitminuspinnumber=0
Limitminuspinnegate=False
Limitpluspinnumber=0
Limitpluspinnegate=False
Homepinnumber=0
Homepinnegate=False
Homedirectionpositive=False
Homeautozero=True
Homingvalue=0
Homingspeedup=500
Homingspeeddown=250
Stepsperunit=200
Velocity=2000
Acceleration=200
Softlimitpositive=0
Softlimitnegative=0
Backlashenable=False
Backlashdistance=0
Homeportnumber=0
Limitminusportnumber=0
Limitplusportnumber=0
Compaccel=240
[Spindlesetupsettings]
IsSpindleinPWMMode=True
SpindlePWMoutpin=14
SpindlePWMoutpinnegate=False
SpindlePWMdirpin=16
SpindlePWMdirpinnegate=False
SpindlePWMfrequency=300
SpindlePWMminpercent=0
SpindlePWMmaxpercent=100
Spindlesteppin=0
Spindlesteppinnegate=False
Spindledirpin=0
Spindledirpinnegate=False
Spindlestepsperunit=500
Spindleacceleration=200
Spindleminvelocity=0.001
Spindlemaxvelocity=20000
Spindlerelaysenabled=True
M3relaypin=14
M3relaypinnegate=False
M4relaypin=16
M4relaypinnegate=False
M3ondelay=300
M3offdelay=300
M4ondelay=300
M4offdelay=300
Floodmistrelaysenabled=True
M7relaypin=1
M7relaypinnegate=False
M8relaypin=17
M8relaypinnegate=False
M7ondelay=300
M8ondelay=300
M9delay=0
SpindlePWMoutport=1
SpindlePWMdirport=1
Spindlestepport=0
Spindledirport=0
M3relayport=1
M4relayport=1
M7relayport=1
M8relayport=1
EncoderApin=0
EncoderAport=0
EncoderBpin=0
EncoderBport=0
Encoderreversedirection=False
EncoderPPR=400
Pulleyratio1=1
Pulleyminvel1=1
Pulleymaxvel1=20000
Pulleyinuse=1
Pulleyratio2=1
Pulleyminvel2=1
Pulleymaxvel2=1
Pulleyratio3=1
Pulleyminvel3=1
Pulleymaxvel3=1
Pulleyratio4=1
Pulleyminvel4=1
Pulleymaxvel4=1
Pulleyratio5=1
Pulleyminvel5=1
Pulleymaxvel5=1
Pulleyratio6=1
Pulleyminvel6=1
Pulleymaxvel6=1
Pulleyratio7=1
Pulleyminvel7=1
Pulleymaxvel7=1
Pulleyratio8=1
Pulleyminvel8=1
Pulleymaxvel8=1
Pulleyratio9=1
Pulleyminvel9=1
Pulleymaxvel9=1
Pulleyratio10=1
Pulleyminvel10=1
Pulleymaxvel10=1
Pulleyratio11=1
Pulleyminvel11=1
Pulleymaxvel11=1
Pulleyratio12=1
Pulleyminvel12=1
Pulleymaxvel12=1
Pulleyratio13=1
Pulleyminvel13=1
Pulleymaxvel13=1
Pulleyratio14=1
Pulleyminvel14=1
Pulleymaxvel14=1
Pulleyratio15=1
Pulleyminvel15=1
Pulleymaxvel15=1
Usepulleys=False
[Generalsettings]
Constantvelocitymode=True
Stopatangle=89
Lookaheadlines=300
Softlimitsenable=False
Homesequence1=Z
Homesequence2=X
Homesequence3=Y
Homesequence4=None
Homesequence5=None
Homesequence6=None
Linearerror=0.03
Cornerserror=0.03
USBbuffersize=0.1
POSDROsdigits=4
Doontoolchange=0
MaxLinearaddlenght=1
MaxLinearunificationlenght=2
Kernelfreq=0
SafeZ=25
G73_backoff=0.4
Maximisescreenonstartup=True
Dwellinseconds=False
Runmodewhenunknowngcode=0
[IOsetupsettings]
Estoppinnumber=0
Estoppinnegate=False
Probepinnumber=0
Probepinnegate=False
Chargepumppinnumber=17
Chargepumppinnegate=False
Chargepumplasermodeon=False
Chargepumpalwayson=True
CurrentHiLopinnumber=0
CurrentHiLopinnegate=False
Indexpinnumber=0
Indexprescaler=1
THCenable=False
THConpin=0
THConpinnegate=False
THCuppin=0
THCuppinnegate=False
THCdownpin=0
THCdownpinnegate=False
THCmin=0
THCmax=10
THCfeed=1000
THCalwayson=False
THCondelay=0
Estopportnumber=0
Chargepumpportnumber=1
CurrentHiLoportnumber=0
Indexportnumber=0
Probeportnumber=0
THConport=0
THCupport=0
THCdownport=0
MPG1pinA=0
MPG1pinB=0
MPG1portA=0
MPG1portB=0
MPG1prescaler=1
MPG1filter=10
MPG1speedmultiplier=10
FROchannel=0
SROchannel=0
JROchannel=0
FROminpercent=0
FROmaxpercent=0
SROminpercent=0
SROmaxpercent=0
JROminpercent=0
JROmaxpercent=0
SPPWMchannel=0
Ana1invarnum=0
Ana2invarnum=0
Ana1outvarnum=0
Ana2outvarnum=0
MPG1attachtoJRO=False
Laseroutputpinnumber=0
Laseroutputportnumber=0
Laseroutputpinnegate=False
THCantidiveenable=False
THCantidivepercent=0
Plasmapierceheight=0
Probepin2number=0
Probeport2number=0
Probepin2negate=False
THCdelayenable=False
THCantidownenable=False
Ana3invarnum=0
Ana4invarnum=0
Ana3outvarnum=0
Ana4outvarnum=0
[Appearancesetupsettings]
2DTLCmarker=True
Viewerundonepathcolor=3381759
Viewerdonepathcolor=-5374161
Viewerrapidpathcolor=16711680
ViewerTCPmarkercolor=16776960
ViewerBackgroundcolor=0
Viewerboundariescolor=16777215
GVgcodecolors=16777215
GVmcodecolors=-233
GVscodecolors=-32513
GVfcodecolors=-21931
GVbackgroundcolor=-12698050
GVactualcodecolor=-16777216
GVactualcodemidlinescolor=-16777216
GVnotinterpretedcodecolor=16711680
GVaxiswordcolor=-8323328
GVcoordinatecolor=-9250052
TCPcone=True
TCPcross=False
RotateTCPwithplaneselection=True
Showzeromark=True
Zeromarkcolor=-16711681
Showmessageonsoftlimits=True
ValidateTextfieldsonEnteronly=True
[Tooltablevalues]
TooloffsetZ0=0
TooloffsetZ1=0
TooloffsetZ2=0
TooloffsetZ3=0
TooloffsetZ4=0
TooloffsetZ5=0
TooloffsetZ6=0
TooloffsetZ7=0
TooloffsetZ8=0
TooloffsetZ9=0
TooloffsetZ10=0
TooloffsetZ11=0
TooloffsetZ12=0
TooloffsetZ13=0
TooloffsetZ14=0
TooloffsetZ15=0
TooloffsetZ16=0
TooloffsetZ17=0
TooloffsetZ18=0
TooloffsetZ19=0
TooloffsetZ20=0
TooloffsetZ21=0
TooloffsetZ22=0
TooloffsetZ23=0
TooloffsetZ24=0
TooloffsetZ25=0
TooloffsetZ26=0
TooloffsetZ27=0
TooloffsetZ28=0
TooloffsetZ29=0
TooloffsetZ30=0
TooloffsetZ31=0
TooloffsetZ32=0
TooloffsetZ33=0
TooloffsetZ34=0
TooloffsetZ35=0
TooloffsetZ36=0
TooloffsetZ37=0
TooloffsetZ38=0
TooloffsetZ39=0
TooloffsetZ40=0
TooloffsetZ41=0
TooloffsetZ42=0
TooloffsetZ43=0
TooloffsetZ44=0
TooloffsetZ45=0
TooloffsetZ46=0
TooloffsetZ47=0
TooloffsetZ48=0
TooloffsetZ49=0
TooloffsetZ50=0
TooloffsetZ51=0
TooloffsetZ52=0
TooloffsetZ53=0
TooloffsetZ54=0
TooloffsetZ55=0
TooloffsetZ56=0
TooloffsetZ57=0
TooloffsetZ58=0
TooloffsetZ59=0
TooloffsetZ60=0
TooloffsetZ61=0
TooloffsetZ62=0
TooloffsetZ63=0
TooloffsetZ64=0
TooloffsetZ65=0
TooloffsetZ66=0
TooloffsetZ67=0
TooloffsetZ68=0
TooloffsetZ69=0
TooloffsetZ70=0
TooloffsetZ71=0
TooloffsetZ72=0
TooloffsetZ73=0
TooloffsetZ74=0
TooloffsetZ75=0
TooloffsetZ76=0
TooloffsetZ77=0
TooloffsetZ78=0
TooloffsetZ79=0
TooloffsetZ80=0
TooloffsetZ81=0
TooloffsetZ82=0
TooloffsetZ83=0
TooloffsetZ84=0
TooloffsetZ85=0
TooloffsetZ86=0
TooloffsetZ87=0
TooloffsetZ88=0
TooloffsetZ89=0
TooloffsetZ90=0
TooloffsetZ91=0
TooloffsetZ92=0
TooloffsetZ93=0
TooloffsetZ94=0
TooloffsetZ95=0
TooloffsetZ96=0
[Workoffset_G54]
WorkoffsetX=715.55
WorkoffsetY=112.818
WorkoffsetZ=-188.561714
WorkoffsetA=57.996809
WorkoffsetB=0
WorkoffsetC=0
[Workoffset_G55]
WorkoffsetX=0
WorkoffsetY=0
WorkoffsetZ=0
WorkoffsetA=0
WorkoffsetB=0
WorkoffsetC=0
[Workoffset_G56]
WorkoffsetX=0
WorkoffsetY=0
WorkoffsetZ=0
WorkoffsetA=0
WorkoffsetB=0
WorkoffsetC=0
[Workoffset_G57]
WorkoffsetX=0
WorkoffsetY=0
WorkoffsetZ=0
WorkoffsetA=0
WorkoffsetB=0
WorkoffsetC=0
[Workoffset_G58]
WorkoffsetX=0
WorkoffsetY=0
WorkoffsetZ=0
WorkoffsetA=0
WorkoffsetB=0
WorkoffsetC=0
[Workoffset_G59]
WorkoffsetX=0
WorkoffsetY=0
WorkoffsetZ=0
WorkoffsetA=0
WorkoffsetB=0
WorkoffsetC=0
[Machinecoords]
MachinecoordsX=718.733714
MachinecoordsY=171.536
MachinecoordsZ=-140.887714
MachinecoordsA=149.111949
MachinecoordsB=0
MachinecoordsC=0
[Tooloffsetcoords]
TooloffsetZ=0
[Systemmessages]
Message0=Valid license key was not found! Application will run in demo mode!
Message1=Firmware update done!
Message2=No UC100 connection was found! Application will run in demo mode!
Message3=Firmware update in progress! Please wait and do not close the application...
Message4=The application lost the connection with the motion controller device. [nl] Check the connection. The application is closing now! [nl] Save offsets?
Message5=A machine axis position software limit was reached. The axis was now stopped.
Message6=The reset logic of the software is active! [nl] Remove the reset condition with pressing the blinking reset button on the screen. [nl] If the reset condition cannot be removed can be due to an external e-stop button is pressed in or a limit switch on the machine tool is active. [nl] Please check the Diagnostics page for the input signals condition.
Message7=The current job workspace is out of the set software limits.[nl] Adjust the softlimits to fit the job extents or disable the softlimits.
Message8=The axis is disabled. To calibrate this axis enable the axis first.
Message9=An internal error occured. The application is closing now.
Message10=Enter a valid distance in absolute value!
Message11=The calculated steps per value was saved.
Message12=Please enter valid data.
Message13=Active fixture:
Message14=Are you sure you want to close?
Message15=
Message16=
Message17=
Message18=
Message19=
Message20=
Message21=
Message22=
Message23=
Message24=
Message25=
Message26=
Message27=The Default profile cannot be deleted!
Message28=File error.Could not delete the profile's macro library!
Message29=Do you really want to delete the profile :
Message30=File error.Could not copy default macros to profile!
Message31=was loaded!
Message32=The axis calibration makes a measurement to calibrate the steps per units resolution value for the machine axis. To abort and close this window press the cancel button.
Message33=Mark the current position of the machine axis. Set the distance and the feedrate on this page and press the OK button to make a movement.
Message34=Measure the travel distance on the machine axis from the previously marked point to the current point. Type the measured value to the field below and press OK.
Message35=The new steps per value was calculated and written to the below field. To save the new value press OK. The process is then finished.
Message36=Switch spindle on first
Message37=Move Z-axis first to safeZ height:
Message38=Make movement with safeZ to:
Message39=Start position(Units):
Message40=Actual steps per Unit:
Message41=Distance to move(Units):
Message42=Feed rate(Units/min):
Message43=Distance measured(Units):
Message44=Steps per Units calculated value:
Message45=The software limits is lower than the safeZ height. Execute the command anyways?
Message46=was created!
[Hotkeysettings]
Keycode1=39
Buttoncode1=147
Keycode2=37
Buttoncode2=148
Keycode3=38
Buttoncode3=149
Keycode4=40
Buttoncode4=150
Keycode5=33
Buttoncode5=151
Keycode6=34
Buttoncode6=152
Keycode7=45
Buttoncode7=153
Keycode8=46
Buttoncode8=154
Keycode9=81
Buttoncode9=155
Keycode10=65
Buttoncode10=156
Keycode11=87
Buttoncode11=157
Keycode12=83
Buttoncode12=158
Keycode13=27
Buttoncode13=130
Keycode14=0
Buttoncode14=0
Keycode15=0
Buttoncode15=0
Keycode16=0
Buttoncode16=0
Keycode17=0
Buttoncode17=0
Keycode18=0
Buttoncode18=0
Keycode19=0
Buttoncode19=0
Keycode20=0
Buttoncode20=0
Keycode21=0
Buttoncode21=0
Keycode22=0
Buttoncode22=0
Keycode23=0
Buttoncode23=0
Keycode24=0
Buttoncode24=0
Keycode25=0
Buttoncode25=0
Keycode26=0
Buttoncode26=0
Keycode27=0
Buttoncode27=0
Keycode28=0
Buttoncode28=0
Keycode29=0
Buttoncode29=0
Keycode30=0
Buttoncode30=0
Keycode31=0
Buttoncode31=0
Keycode32=0
Buttoncode32=0
Keycode33=0
Buttoncode33=0
Keycode34=0
Buttoncode34=0
Keycode35=0
Buttoncode35=0
Keycode36=0
Buttoncode36=0
Keycode37=0
Buttoncode37=0
Keycode38=0
Buttoncode38=0
Keycode39=0
Buttoncode39=0
Keycode40=0
Buttoncode40=0
Keycode41=0
Buttoncode41=0
Keycode42=0
Buttoncode42=0
Keycode43=0
Buttoncode43=0
Keycode44=0
Buttoncode44=0
Keycode45=0
Buttoncode45=0
Keycode46=0
Buttoncode46=0
Keycode47=0
Buttoncode47=0
Keycode48=0
Buttoncode48=0
Keycode49=0
Buttoncode49=0
Keycode50=0
Buttoncode50=0
[Inputtriggersettings]
Pin1=0
Port1=0
Buttoncode1=0
Activelow1=False
Pin2=0
Port2=0
Buttoncode2=0
Activelow2=False
Pin3=0
Port3=0
Buttoncode3=0
Activelow3=False
Pin4=0
Port4=0
Buttoncode4=0
Activelow4=False
Pin5=0
Port5=0
Buttoncode5=0
Activelow5=False
Pin6=0
Port6=0
Buttoncode6=0
Activelow6=False
Pin7=0
Port7=0
Buttoncode7=0
Activelow7=False
Pin8=0
Port8=0
Buttoncode8=0
Activelow8=False
Pin9=0
Port9=0
Buttoncode9=0
Activelow9=False
Pin10=0
Port10=0
Buttoncode10=0
Activelow10=False
Pin11=0
Port11=0
Buttoncode11=0
Activelow11=False
Pin12=0
Port12=0
Buttoncode12=0
Activelow12=False
Pin13=0
Port13=0
Buttoncode13=0
Activelow13=False
Pin14=0
Port14=0
Buttoncode14=0
Activelow14=False
Pin15=0
Port15=0
Buttoncode15=0
Activelow15=False
Pin16=0
Port16=0
Buttoncode16=0
Activelow16=False
Pin17=0
Port17=0
Buttoncode17=0
Activelow17=False
Pin18=0
Port18=0
Buttoncode18=0
Activelow18=False
Pin19=0
Port19=0
Buttoncode19=0
Activelow19=False
Pin20=0
Port20=0
Buttoncode20=0
Activelow20=False
Pin21=0
Port21=0
Buttoncode21=0
Activelow21=False
Pin22=0
Port22=0
Buttoncode22=0
Activelow22=False
Pin23=0
Port23=0
Buttoncode23=0
Activelow23=False
Pin24=0
Port24=0
Buttoncode24=0
Activelow24=False
Pin25=0
Port25=0
Buttoncode25=0
Activelow25=False
Pin26=0
Port26=0
Buttoncode26=0
Activelow26=False
Pin27=0
Port27=0
Buttoncode27=0
Activelow27=False
Pin28=0
Port28=0
Buttoncode28=0
Activelow28=False
Pin29=0
Port29=0
Buttoncode29=0
Activelow29=False
Pin30=0
Port30=0
Buttoncode30=0
Activelow30=False
Pin31=0
Port31=0
Buttoncode31=0
Activelow31=False
Pin32=0
Port32=0
Buttoncode32=0
Activelow32=False
Pin33=0
Port33=0
Buttoncode33=0
Activelow33=False
Pin34=0
Port34=0
Buttoncode34=0
Activelow34=False
Pin35=0
Port35=0
Buttoncode35=0
Activelow35=False
Pin36=0
Port36=0
Buttoncode36=0
Activelow36=False
Pin37=0
Port37=0
Buttoncode37=0
Activelow37=False
Pin38=0
Port38=0
Buttoncode38=0
Activelow38=False
Pin39=0
Port39=0
Buttoncode39=0
Activelow39=False
Pin40=0
Port40=0
Buttoncode40=0
Activelow40=False
Pin41=0
Port41=0
Buttoncode41=0
Activelow41=False
Pin42=0
Port42=0
Buttoncode42=0
Activelow42=False
Pin43=0
Port43=0
Buttoncode43=0
Activelow43=False
Pin44=0
Port44=0
Buttoncode44=0
Activelow44=False
Pin45=0
Port45=0
Buttoncode45=0
Activelow45=False
Pin46=0
Port46=0
Buttoncode46=0
Activelow46=False
Pin47=0
Port47=0
Buttoncode47=0
Activelow47=False
Pin48=0
Port48=0
Buttoncode48=0
Activelow48=False
Pin49=0
Port49=0
Buttoncode49=0
Activelow49=False
Pin50=0
Port50=0
Buttoncode50=0
Activelow50=False
[Outputtriggersettings]
Pin1=0
Port1=0
LEDcode1=0
Invert1=False
Pin2=0
Port2=0
LEDcode2=0
Invert2=False
Pin3=0
Port3=0
LEDcode3=0
Invert3=False
Pin4=0
Port4=0
LEDcode4=0
Invert4=False
Pin5=0
Port5=0
LEDcode5=0
Invert5=False
Pin6=0
Port6=0
LEDcode6=0
Invert6=False
Pin7=0
Port7=0
LEDcode7=0
Invert7=False
Pin8=0
Port8=0
LEDcode8=0
Invert8=False
Pin9=0
Port9=0
LEDcode9=0
Invert9=False
Pin10=0
Port10=0
LEDcode10=0
Invert10=False
Pin11=0
Port11=0
LEDcode11=0
Invert11=False
Pin12=0
Port12=0
LEDcode12=0
Invert12=False
Pin13=0
Port13=0
LEDcode13=0
Invert13=False
Pin14=0
Port14=0
LEDcode14=0
Invert14=False
Pin15=0
Port15=0
LEDcode15=0
Invert15=False
Pin16=0
Port16=0
LEDcode16=0
Invert16=False
Pin17=0
Port17=0
LEDcode17=0
Invert17=False
Pin18=0
Port18=0
LEDcode18=0
Invert18=False
Pin19=0
Port19=0
LEDcode19=0
Invert19=False
Pin20=0
Port20=0
LEDcode20=0
Invert20=False
Pin21=0
Port21=0
LEDcode21=0
Invert21=False
Pin22=0
Port22=0
LEDcode22=0
Invert22=False
Pin23=0
Port23=0
LEDcode23=0
Invert23=False
Pin24=0
Port24=0
LEDcode24=0
Invert24=False
Pin25=0
Port25=0
LEDcode25=0
Invert25=False
Pin26=0
Port26=0
LEDcode26=0
Invert26=False
Pin27=0
Port27=0
LEDcode27=0
Invert27=False
Pin28=0
Port28=0
LEDcode28=0
Invert28=False
Pin29=0
Port29=0
LEDcode29=0
Invert29=False
Pin30=0
Port30=0
LEDcode30=0
Invert30=False
Pin31=0
Port31=0
LEDcode31=0
Invert31=False
Pin32=0
Port32=0
LEDcode32=0
Invert32=False
Pin33=0
Port33=0
LEDcode33=0
Invert33=False
Pin34=0
Port34=0
LEDcode34=0
Invert34=False
Pin35=0
Port35=0
LEDcode35=0
Invert35=False
Pin36=0
Port36=0
LEDcode36=0
Invert36=False
Pin37=0
Port37=0
LEDcode37=0
Invert37=False
Pin38=0
Port38=0
LEDcode38=0
Invert38=False
Pin39=0
Port39=0
LEDcode39=0
Invert39=False
Pin40=0
Port40=0
LEDcode40=0
Invert40=False
Pin41=0
Port41=0
LEDcode41=0
Invert41=False
Pin42=0
Port42=0
LEDcode42=0
Invert42=False
Pin43=0
Port43=0
LEDcode43=0
Invert43=False
Pin44=0
Port44=0
LEDcode44=0
Invert44=False
Pin45=0
Port45=0
LEDcode45=0
Invert45=False
Pin46=0
Port46=0
LEDcode46=0
Invert46=False
Pin47=0
Port47=0
LEDcode47=0
Invert47=False
Pin48=0
Port48=0
LEDcode48=0
Invert48=False
Pin49=0
Port49=0
LEDcode49=0
Invert49=False
Pin50=0
Port50=0
LEDcode50=0
Invert50=False
[CAMsettings]
Tooldia=6
Startdepth=0
Cutdepth=-1
Cutperpass=1
SafeZ=25
Feedrate=1000
Tooloverlap=50
Plungerate=400
Spindlespeed=5000
Arctolerance=0.01
[Laserengraveplugin]
workpiecewidth=50
workpieceheight=50
keepaspectratio=True
Yscandistance=0.2
Feedrate=1000
Originsetting=7
[Plugins_enabled]
Debugger.dll=False
Diagnostics.dll=False
Laserengrave.dll=False
Plugintest.dll=False
Webcamera.dll=False
Printer3D.dll=False
UCR200Plugin.dll=False
Xbox360controller.dll=False
Scope.dll=False
AutoLevelerCA.dll=False
Modbusmaster.dll=False
XHC-HB04_pendant.dll=True
[Plugins_callstartup]
Debugger.dll=False
Diagnostics.dll=False
Laserengrave.dll=False
Plugintest.dll=False
Webcamera.dll=False
Printer3D.dll=False
UCR200Plugin.dll=False
Xbox360controller.dll=False
Scope.dll=False
AutoLevelerCA.dll=False
Modbusmaster.dll=False
XHC-HB04_pendant.dll=False
[Macroloops]
Macroloopautorun0=False
Macroloopnumber0=0
Macroloopautorun1=False
Macroloopnumber1=0
Macroloopautorun2=False
Macroloopnumber2=0
Macroloopautorun3=False
Macroloopnumber3=0
Macroloopautorun4=False
Macroloopnumber4=0
Macroloopautorun5=False
Macroloopnumber5=0
Macroloopautorun6=False
Macroloopnumber6=0
Macroloopautorun7=False
Macroloopnumber7=0
Macroloopautorun8=False
Macroloopnumber8=0
Macroloopautorun9=False
Macroloopnumber9=0
Macroloopautorun10=False
Macroloopnumber10=0
Macroloopautorun11=False
Macroloopnumber11=0
Macroloopautorun12=False
Macroloopnumber12=0
Macroloopautorun13=False
Macroloopnumber13=0
Macroloopautorun14=False
Macroloopnumber14=0
Macroloopautorun15=False
Macroloopnumber15=0
Macroloopautorun16=False
Macroloopnumber16=0
Macroloopautorun17=False
Macroloopnumber17=0
Macroloopautorun18=False
Macroloopnumber18=0
Macroloopautorun19=False
Macroloopnumber19=0
Macroloopautorun20=False
Macroloopnumber20=0
Macroloopautorun21=False
Macroloopnumber21=0
Macroloopautorun22=False
Macroloopnumber22=0
Macroloopautorun23=False
Macroloopnumber23=0
Macroloopautorun24=False
Macroloopnumber24=0
Macroloopautorun25=False
Macroloopnumber25=0
Macroloopautorun26=False
Macroloopnumber26=0
Macroloopautorun27=False
Macroloopnumber27=0
Macroloopautorun28=False
Macroloopnumber28=0
Macroloopautorun29=False
Macroloopnumber29=0
Macroloopautorun30=False
Macroloopnumber30=0
Macroloopautorun31=False
Macroloopnumber31=0
Macroloopautorun32=False
Macroloopnumber32=0
Macroloopautorun33=False
Macroloopnumber33=0
Macroloopautorun34=False
Macroloopnumber34=0
Macroloopautorun35=False
Macroloopnumber35=0
Macroloopautorun36=False
Macroloopnumber36=0
Macroloopautorun37=False
Macroloopnumber37=0
Macroloopautorun38=False
Macroloopnumber38=0
Macroloopautorun39=False
Macroloopnumber39=0
Macroloopautorun40=False
Macroloopnumber40=0
Macroloopautorun41=False
Macroloopnumber41=0
Macroloopautorun42=False
Macroloopnumber42=0
Macroloopautorun43=False
Macroloopnumber43=0
Macroloopautorun44=False
Macroloopnumber44=0
Macroloopautorun45=False
Macroloopnumber45=0
Macroloopautorun46=False
Macroloopnumber46=0
Macroloopautorun47=False
Macroloopnumber47=0
[Statistics]
TotalM3s=72
TotalM4s=31
TotalM7s=21
TotalM8s=23
Totaltimedays=3
Totaltimehours=4
Totaltimeminutes=43
Totaltimeseconds=40
M3timedays=0
M3timehours=2
M3timeminutes=11
M3timeseconds=40
M4timedays=0
M4timehours=0
M4timeminutes=1
M4timeseconds=9
Cyclestimedays=0
Cyclestimehours=0
Cyclestimeminutes=10
Cyclestimeseconds=32
TotaldistX=9224
TotalcutX=1830
TotaldistY=10630
TotalcutY=2656
TotaldistZ=4344
TotalcutZ=414
TotaldistA=6258
TotalcutA=12
TotaldistB=0
TotalcutB=0
TotaldistC=0
TotalcutC=0
[Digitizesettings]
Addaxisnames=False
Xinclude=True
Yinclude=True
Zinclude=True
Ainclude=False
Binclude=False
Cinclude=False
Commaseparation=False
Filenametosave=C:\UCCNC/Example_codes/Digitize.txt
Numberofdigits=4
Probedia=0
Clearfilenamewhenfinished=False
[RFHsettings]
Switchspindlemode=1
Doinitialmoveswithrapid=False
[XHC]
Filter=5
SpeedMultiplier=20
Macro1=500
Macro2=500
Macro3=500
Macro6=500
Macro7=500
Macro1FunctionEnable=True
Macro2FunctionEnable=True
Macro3FunctionEnable=True
Macro6FunctionEnable=True
Macro7FunctionEnable=True
Macro1Function=0
Macro2Function=0
Macro3Function=0
Macro6Function=0
Macro7Function=0
Re: Soft Limit errors appear all the time
Posted:
Tue May 23, 2017 2:57 pm
by Guenter_Schmied
This profile was done at installation, it is basically the same I am
using now, except I did 9million999999 and -9million999999 in the
softlimits of Axis X Y Z and A , the ones I am using.
I did also a rounding at stepsperunit in each axis to reduce the chance this
could generate any strange behavior (f.e. 318.18181818 is now 318.1812)
Hope you can help me !
Best regards
Guenther