UCCNC with UB1 Sanity Check

Post anything you want to discuss with others about the software.

Re: UCCNC with UB1 Sanity Check

Postby ger21 » Sun Jun 21, 2020 12:40 pm

On your 24V power supply, you have two wires connected to +24V, and none connected to 0V.

And you have +24V connected to the 0V terminal on the UB1, and the 24V terminal on the UB1 wired to the X103 terminal?
24V on the UB1 should be wired to +24V from the power supply, and 0V on the power supply (-) should be wired to the 0V on the UB1 that you are showing +24V connected to.

Not sure what you are trying to do here?
Gerry
UCCNC 2022 Screenset - http://www.thecncwoodworker.com/2022.html
ger21
 
Posts: 2714
Joined: Sat Sep 03, 2016 2:17 am

Re: UCCNC with UB1 Sanity Check

Postby spumco » Sun Jun 21, 2020 10:11 pm

E-stop wiring appears to be oddand as Ger pointed out you aren't supposed to send 24vdc to UB1/X103.

1. It looks like the E-stop is an NO switch, not a standard NC switch.
2. If the E-stop is activated, it kills 24vdc to UB1, as well as the CM3 contacts, as well as UB1-X103
3. Not sure what the point of S3 is, unless you want a separate switch to turn off the drive and VFD bus power. Or were you attempting a 'reset' type switch?

If this is correct, then there is no point signaling X103 as you've just turned off the UB1 completely.

I think you might want to consider the following scheme:

1. Momentary NO - "ON"
2. Momentary NC - "OFF"
3. Momentary NO - "RESET"
4. Latching NC w/2 sets contacts - "ESTOP"
5. DPDT Relay - "R1" (additional relay #1)
6. DPDT Relay - "R2" (additional relay #2)

R1 is wired as a holding relay using "ON" and "OFF" - this prevents unintended restarts after a power interruption.
R1 Input contacts: 24VDC from breaker/fuse
R1 Output contacts: to R2 input contacts and anything else you want to feed 24VDC when in an E-stop condition (red light, VFD logic, ect)

R2 is wired as a holding relay with "RESET" (set #1 NC contacts) and "ESTOP" to the relay coil.
R2 Input contacts: 24VDC from R1 output
R2 Output contacts: 24VDC to UB1/NO3

UB1/CM3 to contactor coil.
"ESTOP" (set #2 NC contacts) UB1/X103 and UB1/0V for signaling UB1 safety circuit (UB1/X104 to /X109) and UCCNC.

In this scheme when you press the ON button, the UB1 is powered up, but the drives do not power up and if the e-stop is engaged UB1/UCCNC knows there is an e-stop condition.
To power the drives, you unlatch (close contacts) ESTOP, and then press RESET. This energizes coil of C1 and powers the drive/VFD bus.

The fundamental idea with this scheme is that:
1. User and UCCNC/UB1 can assert an e-stop event, but
2. UCCNC/UB1 cannot reset from an e-stop event without human intervention via mechanical relay and the RESET button.
Relay Holding Circuit.jpg