If only restarting Windows helps then maybe, something remains in memory when you exit UCCNC. Try the following: start UCCNC, test spindle, exit UCCNC, start task manager, try to find stuck UCCNC process by pressing U repeatedly until it goes around all processes starting with U. If you find UCCNC then there is something which prevents all threads to close. You can stop the process and try again. If it works then you found the problem. (In the past I had the same problem with a plugin development. :))

Re: MODBUSEZ Plugin

PostPosted: Thu May 17, 2018 12:20 pm
by Dan911
Hmmm, I think it's very safe to assume it's not your RS485 connection. What seems to be happening is something is changing the way frequency is calculated, the only thing within UCCNC that can do this besides what I already posted to check is enabling pulleys. Also maybe a cultureinfo problem??

Knowing the different issue that's making you restart UCCNC can possibly help trouble shoot your problem since it's obviously related.

Dan

Re: MODBUSEZ Plugin

PostPosted: Sun Nov 25, 2018 1:05 pm
by andrewwong2000
I've just installed MODBUS EZ with my Powtran 9130 VFD, and can get the spindle to spin clockwise & ccw (following Dan's previous post on the subject).

But I can't seem to set the frequency ( using method one in the VFD manual).. it just seems to ignore any spindle setting from UCCNC.

As the start/stop works OK, I'm guessing it's probably some setting on the VFD.

Appreciate if anyone can suggest why the VFD accepts start/stop but not the freq command ?

Thanks,
Andrew

Re: MODBUSEZ Plugin

PostPosted: Sun Nov 25, 2018 5:05 pm
by Dan911
Dan911 wrote:Alex please look at snip I taken from your manual, your configured for second option using frequency address 1000 and your VFD is not going to accept the format ModbusSZ plugin is sending frequency.

You need to use first option using frequency address 0001. There's also a setting in your VFD for frequency resolution (F0.02) 1- 0.1hz and 2 - 0.01hz. If F0.02 is set to 1 than don't check box in ModbusEZ "Spindle Setup"

Use the new final V15 plugin I uploaded in previous post.

Dan

The attachment PT manual.JPG is no longer available


Your frequency address needs to be set to>>>>>>>>>>>>>>> 0001
Read the quote for frequency resolution, make sure that ModbusEZ corresponds with VFD settings.

Your VFD needs to be set to Keyboard sets frequency see snip of manual below.

Powertran 9100.JPG

Re: MODBUSEZ Plugin

PostPosted: Wed Nov 28, 2018 2:40 pm
by andrewwong2000
Hi Dan,

Thanks heaps.. turned out I had a conflicting function set up.

VFD & Plug in works great!

Cheers,

Andrew

Re: MODBUSEZ Plugin

PostPosted: Sat Dec 15, 2018 5:36 pm
by mrping
Hi there,

New UCCNCer here that run a Brother TC225 retrofitted with UCCNC. I have some problems with modbus so I tried this plugin. I tried Machtric S800 settings, but my VFD is a Machtric S3800 (more advanced version with closed loop).

When I start UCCNC my motor starts spinning, where it in the middle stops spinning, where it starts spinning again 1 sec after. MODBUSEZ plugin tells me im connected.

M3/M4/M5 doesnt do anything. Not S1000/6000 either.
Havent got a real modbus manual for my VFD :(

Re: MODBUSEZ Plugin

PostPosted: Sat Dec 15, 2018 5:55 pm
by mrping
This is the Machtric S3800D manual I have.

Re: MODBUSEZ Plugin

PostPosted: Sat Dec 15, 2018 7:08 pm
by mrping

Re: MODBUSEZ Plugin

PostPosted: Sat Dec 15, 2018 7:49 pm
by dezsoe
Hello mrping, What UCCNC version do you use? I watched your video and it seems a very old version. I'm not sure if the plugin requires a newer version, just remarked. (If I can recall, the last version with this startup screen was 1.2037, the latest stable version is 1.2049.)

Re: MODBUSEZ Plugin

PostPosted: Sat Dec 15, 2018 10:07 pm
by Dan911
Thanks Dezsoe... and you are correct. I don't remember off hand when the overridden field was added but 49 he will be good to go.