It took me a while but here is a setup that may help others:
VFD BRAND: LSIS
Model : LSLV-C100
User Manual:
http://www.wolfautomation.com/media/pdf ... manual.pdftips:
1) Do all your test with the "MODBUS Master" plugin NOT "MODBUS EZ"..it's MUCH faster to do trial and error with because you don't have to restart software every time a parameter is changed.
When confident then try your settings in ModbusEZ...
2) what the manual shows for the registers : 0x005 frequency reference addr (No!) , 0x006 "run address" (No!)
THE actual DECREMENTED register address values that the Modbus communication must use: 0x004 frequency reference addr (YES!) , 0x005 run address (YES!)
No where, in the manual, could i find mention of decrementing the address, discovered strange behavior when testing with the "Modbus Master" plugin and some intuitive googling.
From the manual configuring the inverter via the keypad to use Modbus like this:
Screenshot of ModbusEZ that worked for me:
(Note that the Amp/current register address is also decremented from 0x009 to 0x008 ! )